DF-1 RS232 protocol problem with bit 4 and 12
chudchud
Jul 2008
los angeles
I'm connecting directly to a SLC 5/04 using the RSLinx DF-1 RS232 driver and going online using RSLogix 500.
I've also setup a protocol analyzer to capture the data stream going back and forth.
When I set bit 4 in the N9:2 register, I see the following mask and data values in the protocol analyzer:
Setting N9:2/4 produces:
Mask: 10 10
Data: 00 10 10 10
Setting N9:2/12 produces:
Mask: 00 10
Data: 10 00 10 10
I've tried all other remaining bits in this word and they all produce the expected results:
For example,
Setting N9:2/3 produces:
Mask: 08 00
Data: 08 00
Is there something being added to the mask and data values for bit 4 and bit 12 that I'm not aware of?
Any help would greatly be appreciated. Thank you.
Try reading an ordinary integer register with the value of 16; you should see the same kind of behavior.
It's called "DLE Escaping" and is described in the DF1 reference manual.
Because DLE (10 hex) is a special character in DF1 command frames, when it occurs in an address, data, or mask field the controller or software has to represent that the occurence is not a DLE command. It does so by repeating the 10(hex) twice.
DLE Escape occurences are frequently overlooked or mishandled by third-party DF1 drivers that I have used and troubleshot in the past. If you are writing your own DF1 driver, you need to understand and account for DLE Escaping in all cases.
Dear All, I want to communicate with Arburg Selogica controller v3.09 of an old Arburg injection molding machine. The protocol by which this...
2,625
Does anyone have any resources that may give specifics about the RS232 protocol from an Ishida DACS-CW? I'm going to most likely use a Comtrl...
3,627
Hey guys, I am looking for a solution and running against walls since weeks... I have to connect a meterological station with ABB microSCADA...
1,989
Hi, My company builds machinery on which we use Allen-Bradley ControlLogix PLC's. We use drive speed controllers that have their own...
4,501
Hi Chaps, I have a SLC 5/04 configured with the RS 232 port (Channel 0) as DH485 protocol, am I right in thinking that I need to use the PIC...
5,755