Other thing to be aware of with the PIC driver in RSLinx
- the max number if is important also. As suggested before, need to see how the PLC com port is set up. Not only baud rate and address, but the max number setting has to match. These are all things that the "auto configure' cant determine. You have to have all this set in RSLinx config to match the setup on PLC port.
- About only way to see how the SLC port is set up is to have a copy of the program. Or...get online to the SLC thru the other port.
- the max number if is important also. As suggested before, need to see how the PLC com port is set up. Not only baud rate and address, but the max number setting has to match. These are all things that the "auto configure' cant determine. You have to have all this set in RSLinx config to match the setup on PLC port.
- About only way to see how the SLC port is set up is to have a copy of the program. Or...get online to the SLC thru the other port.