Hi all,
Our network has a micrologix 1200 conected by a 1761-net-eni to ethernet, also on this same ethernet network lives a control logix processor which also has a dh+ network attached to it attached to this dh+ network is several plc5 processors. I need to message from the plc5 processor that lives on the DH+ network to the micrologix 1200 that lives on the ethernet network.Ideally I would like the 1200 to initiate a read from the plc5.Is this possible? if so any ideas on how I might do it? Also bear in mind the plc5 is an old revision and doesn't support multihop comms.Any help would be appreciated.
Tom
We have almost the exact same setup on some of the machines where I work. If you're using RSLinx, you should be able to set up an ethernet driver to the micrologix and the contrologix. I know there is a way to create a direct communications path between the PLC on the DH+ and the micologix on the ethernet, but I've never tried it myself. It is covered in Rockwell publication ABT-1756-TSJ50 under the section called "Creating and Entering a Numeric Communications Path".
If you don't mind using the contrologix as a "pass-through", once you've got the ethernet driver set up you can just have the contrologix read from the PLC, and then have the micrologix read from the contrologix.
I'm admittedly a little wet behind the ears yet, so if anything I just said was dead wrong, somebody please correct me, but I'm pretty sure either of those ideas will work if set up properly.
Hello, I am attempting to set up Ethernet coms between a L06CPU and a Cmore EA9-T6CL HMI via Ethernet with no success. There is no Ethernet...
1,892
Hi, I am working with a L35E and a Yaskawa VFD using Ethernet coms. I use AB's Generic Ethernet Module to communicate. Is there a Tag that I can...
1,763
All, I'm looking for suggestions for wireless Ethernet solutions for linking two AutomationDirect PLCs (probably DL-06's) and a C-More...
4,439
Hi guys, This morning I was called over to a machine that has been running fine for months. The screen had ?????s everywhere so that I know...
3,253
I have a Mitshubishi FX2n with an FX2nc-enet-apd ethernet card which I am trying to connect 2 concurrent opc servers to Problem is that the...
2,418