HI guys!
This is the first time I am here!
Would like know
1. We want to synchronize 3 , 600 KVA Gensets, later we may add another 600 KVA or higher.

Which is the best Woodward synchronizer suitable for Auto mains failure panel (AMF), Auto load sharing and synchronizing.

2. what is the differance between easyGen 3200 and EGCP2

Please suggest me the best configuration.

Thanks and Regards

Raghu
India
 
Use the EasyGen - it is the future direction and is cheaper. You can also get one without a screen. Lot less wiring as you can mmount it in the panel and not have to wire evrything to the door. Just use Modbus RTU to monitor everything into the PLC. They do have a remote screen on the way by the way. That will remove the need to wire evything to the door also.

My major objection to the EGCP2 is that you need a password to reset any alarms - absolute pain in the you know what when a set has shut down in the middle of the night..
 
Easygen 3200

please,
i need to monitor and control the Easygen 3200-5 since a PC located 60 meters far,
What port is the appropiate to use ??
RS 232 , RS 485 ??
The RS 232 works well with the Toolkit software,
Does the RS 485 need any software ?? i have trouble to communicate through this port
best regards,
 
I presume you are interfacing with a PLC - you do not mention.
Over that distance you will need to use either RS422 or RS485 - RS232 just won't cut it.
I have not used the RS485 port at this stage but it should work OK. Protocol is Modbus RTU. You will need to set up the port with the configuration software first. Then test the port with Modscan to see if you can communicate with it.
Watch out for A and B - A is generally negative but some manufacturers reverse A and B.
 
You will still need to use RS422 or RS485. You will also need software to talk Modbus RTU to the easYgen. I normally use Citect SCADA for this.
 

Similar Topics

Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
Replies
7
Views
1,426
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
Replies
28
Views
4,058
Good Morning , I have 2 Frequency Drive panels to build and commission . It is for 2 pump systems . Just wondering , what is the...
Replies
4
Views
1,978
Hi Experts, Good day! What are the differences between PCS7 SIMATIC Batch and PM Control? Do you have any manual like "Getting Started "...
Replies
0
Views
821
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
Replies
9
Views
2,844
Back
Top Bottom