Dl240 with analog 4-20 input

Thanks guys, I have it working! Had to connect my loop simulator - to + and + to -, and it runs a very accurate 0 to 4095 (100%).

Thanks so much!
 
Your data will arrive in V2000, V2001, V2002, V2003.
LDA O2000, OUT V7673 (V7673 is the module's pointer to the data location (V2000)).

It looks kinda cryptic because it is. This is definitely NOT the only device that uses cryptic configuration / programming style.

I play with this not because I have to, but because I want to learn it. RSLogix is so much easier, and way more expensive! I'll get used to this eventually... maybe!

I've got it displaying (thru the DATA icon) values and am using a loop simulator to input 4-20 ma. Works great and accurate!

Thanks so much for helping me get this going!
 