DL440 analog inputs
nathan.slade
Mar 2010
n.s.w
69
Hi all.
Imafter a litle help. im trying to workout how the analogs work in direct soft. I have a dl440 and f4-08ad setup on the benc but am haveing trouble with the prgraming. could someone walk me through it. wick program to show the 8 inpts connected to pt100's usin 4-20ma would be great.
thanks all
Do you have the module's manual, available here?
You have to follow the example code to recover the readings from the 16 X inputs one at a time. Since you have the DL440 follow the program example in the section named 'Reading Values, DL440/450' On successive program scans one channel is read and stored in an 8 place table.
You mention PT100 and 4-20ma. Do you have convertors which take the PT100 sensors as inputs and send out a 4-20ma signal which is attached to the analog input module? It is not practical to connect the PT100 sensors directly to the input module.
Hi mate. sorey about the spelling. ****ty comp at work. I have read the manual andam haveing truble with under standing how to adress and the vmemory part. i have mainly used a/b plc's and under stand the scaling. all iwont to d at the moment is to have a analoge card in slot 1 hocked up to a 4-20Ma signal and scale it to a 0-100 deg celcius figure for now and under stand how we get there. i'm doing this on my own at work so when i get stuck in the middle of the night with no one to call i can work out whats going on.
wheres waldo? can YOU find my error? automation direct, k sequence. cmore hmi wont communicate with dl 440 plc video...
2,144
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
39
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
130
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
143
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,213