I’m not getting any RAW data at this Variable V7677. I loaded 0400 into V7667. The electric wiring is done correctly as per Analog Manual and so was the setting for the TC33.
The TC33 is showing the correct temperature but the PLC is not. Anyone knows why?
Hardware:
AD 250 CPU
AD TC33 Temperature Controller
AD F2-4AD2DA 4-Ch. In / 2-Ch. Out Combination Analog
2 Wire Type J Thermocouple
Software:
DirectSoft v4 built 24
Andy
Could be the card
Andy i believe you need a F2-04THM card with your thermocouple input. I could be wrong??
:site:
Hello,
In Koyo, You have to make some Configuration for analog I/Os
For example: in DL05
V7701 is a pointer for the first AI channel (It should hold the address you want to store the first analog input channel in)
V7700 "tells" the PLC two things:
1- Number of Analog I/Os
2- numbering system required (BCD or Binary)
So check the manual for the DL205 (Option modules manual), It should be like that and check that you did it right.
Note: I read your post so quickly, so you I may pointed you to things you don't need or you already did it all, So forgive me If I told you things you alreasy know.
They are installed in a control panel that was made in France and are intended for the termination of analog inputs. Each of the red capped...
430
Need some help here (again). I tried to download my HMI to the PLC and I get this error message about a missing file. Can anyone help?
835
Hi there, I need to work on a GE series 5 PLC which need DOS based Logic Master 5, it seems like nowhere I can purchase this software anymore...
960
Would like to ask .. if anyone here know about creating own library or function block on ProWORX NxT ? I have a backup of ProWORX NxT project...
1,058
Does anyone have a spare PacDrive part# LMC600CBD10000? Not necessarily for sale, but to do a bench test. I have a CF image file, and I'd like...
1,266