Does the last octet mean anything? RSLinx - EtherNet/IP - Browse Remote Subnet
theColonel26
Feb 2014
West Michigan
785
Technically the network's address is 0, but why does it give you the option in the first place?
Strictly speaking, the network address is 0 IF you have a 255.255.255.0 (or /24) subnet mask. If you have something like 255.255.255.192 (/26) then you could have 192.168.0.0, .64, .128, and .196.
Granted, you almost always have a /24 or larger, but you COULD do less if you wanted; unless the equipment is so old it only lets you choose class A/B/C.
55
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
60
I am trying to connect with a Schneider plc which has a firmware version only available in Somachine v4.2. In Machine expert After taking upload...
129
They are installed in a control panel that was made in France and are intended for the termination of analog inputs. Each of the red capped...
444