Lifetime Supporting Member + Moderator
Yes it is exactly what you have done allready.
As it seems that it is possible to do it (because the other guy says so), and because we cannot pinpoint where your two previous projects (integrated and standalone) works and doesnt work, I suggest that we start all over again.
Reset both CPUs.
Try to make one project with S7-400 and S7-300 and make a connection between the two in S7-400. Then download to S7-400 only.
Then make another project with S7-300 only and download to S7-300.
If PUT and GET works, then repeat the whole thing with fresh new programs but alter the Profibus addresses.
If it still works, then I guess it can be assumed it will work in general.
As it seems that it is possible to do it (because the other guy says so), and because we cannot pinpoint where your two previous projects (integrated and standalone) works and doesnt work, I suggest that we start all over again.
Reset both CPUs.
Try to make one project with S7-400 and S7-300 and make a connection between the two in S7-400. Then download to S7-400 only.
Then make another project with S7-300 only and download to S7-300.
If PUT and GET works, then repeat the whole thing with fresh new programs but alter the Profibus addresses.
If it still works, then I guess it can be assumed it will work in general.