E3 Plus DeviceNet through 1788-EN2DN
SIS_Brady
Jan 2018
Mississippi
Hello,
I have an E3 Plus module that I am having issues with. We have ethernet coming from the processor (L32E) and going to a 1788-EN2DN. From the EN2DN, we go devicenet into the field. All nodes work properly except for one. When the node is told to run, the motor contactor chatters. I have switched the node with a working nodes' number and it works correctly. With that said, that takes the possibility of a bad E3 Plus module or bad devicenet cable out of the equation. Has anyone ever seen this?
Please help, we are about to get busy and I am needing this working correctly.
Can you explain exactly what you mean by that ? Did you physically swap out the E3 Plus with another unit, or did you change the node number on the E3 Plus so that it was the same as a working unit (while that unit was unplugged) ?
In general, if there's a network signal problem then an E3 will fault on network loss. Even if it was configured to just turn off the output (but not fault) on connection loss, it takes a couple of seconds for a DeviceNet slave connection to time out and re-establish; it would not be a "chattering" output.
A "chattering" output sounds like a damaged E3 Plus output relay, or a mis-wired coil on the contactor (like if a normally closed Aux contact were mis-wired in series).
Put a Counter on the Output for the E3+ inside your PLC program to be sure it's not being told to turn off/on rapidly.
Hello, I have a company that uses e3 Pluses with devicenet that talks to the L63 processor over a 1788-cn2dn device. E3 Pluses aren't being sold...
1,696
Hi folks, First of all, Merry Christmas and Happy New Year to everyone! I'm the lucky heir (as process engineer) to a dated process that...
2,725
How do you transfer the runtime .MER to a DeviceNet PVPlus? If the only way is a USB stick, I think I might drop this thing off a bridge.
1,163
I have a system controlling two 1336 plus drives via SLC 5/04 and 1747-SDN scanner. The logic issues the start command, and the corresponding...
1,632
Hi Is my first time I post in this forum and also Im new in all this things of PLC programming so I hope someone can help me with this problem...
5,722