hi all
i run RSLogix 5000 to download a program to Logix5555
i use 1756-IB16D for digital input
in the I/O configuration i choose that module, and choose compatible keying
i also click the "major fault on controller when connection failed in run mode" option
when i go to run mode, after a few second, an fault occurs
the fault error code is
error 23 : at least one required connection is not established before going in to run mode
then i try to change the electronic keying to disable keying option, run it again, and it works
why is it?
is there something wrong in the I/O configuration?
i think i choose the right module
i appreciated ur respond
thx a bunch
When you select "compatible keying" the processor will accept any module in the slot that is a 1756-IB16D and has the same major revision as the one you picked from the list. I suspect that you accepted a revision 3.xx module in the application but have revision 2.xx hardware in the slot. You can't change the major revision in the application; you'll have to delete the module and rs-select it, remembering to pick revision 2.
Hi Everyone, Is it Possible to change the Power flex 753 Drive Electronic keying when PLC is in Online, If So If I change the Electronic keying...
409
Sorry its probably a stupid question. I have version 1.008 PF527 which going to be replaced with a FW Version 2.001 Unit. I have version 32 logix...
1,497
I have a CompactLogix running RSL5k v.20.05 that is controlling a case packing machine. I added a Keyence vision sensor/camera to this controller...
20
8,998
1st post for me here..... Control Logix v20 RSL5K Powerflex 755 Ethernet Comms Hirachmann managed Can anybody tell me what the disadvantages of...
1,816
RslLogix 5000 In I/O configuration/ Module Properties and Electronic Keying what do the options of “Compatible Mode, Disable Keying, Exact Match”...
27,818