ENBT Module Problem

satish.manda

Member
Join Date
Feb 2014
Location
Hyderabad
Posts
8
Hi this satish,

I have a problem in the ENBT module. The link status led was steady green on the module indication & stopped communicating with other device. When i removed and replugged the ethernet cable to that module. It started communicating.
Can anyone help....... what could be the reason for that.
When i checked the ENBT diagnostic on explorer the CPU usage shown to around 80 to 92.6% max. will that cause the problem.
 
Yes, the 80-92% CPU usage is a problem and your solution of unplugging/plugging to fix points to this being the problem. You need to decrease the CPU usage.
 
You can lower IO scan rates. Most don't need to be any faster then 100ms. Also make sure any messages (MSG) blocks are no faster then 100ms. Using the XIO of a MSG.DN bit to trigger a message will kill your network in a hurry.
 

Similar Topics

Hello All, Thanks in advance... Friends today I am adding a New EthereNet Module ENBT through RSLogix 5000 software..but after adding details...
Replies
4
Views
3,809
Allen Bradley Control Logix 5561 Series Model 1756-L61 Series B Controller. Panel View Plus 1000 HMI Touch Screen. Communication Module 1756 ENBT...
Replies
1
Views
4,602
I configured Ethernet module with BOOTP/DHCP . I follow the Ethernet's manual. After Add to Relation List ,i press disable BOOTP/DHCP but no effect.
Replies
5
Views
2,212
I have a spare ENBT module on a remote rack at slot 3 that communicates to a privately addressed EN2T module at 192.168.1.2 on the main rack via...
Replies
5
Views
1,720
Hi All, I have a 1768 L43S Guardlogix controller FW 19 with a 1768-ENBT A module in the rack. This unit was purchased 2nd hand, and the...
Replies
1
Views
2,731
Back
Top Bottom