Encoder PPR selection
No no no!!!!
@Kid: Pick one, standardize on it, live with it.
99.875% of "Drive" applications run perfectly well with either a 1000 or 1024 ppr encoder.
A drive controlling an constant speed conveyor only needs PI control. Yes you can get by with a lot fewer counts per revolution because the derivative gain is not required but when controlling positions, velocity and accelerations you need to use the derivative gain and the ability to estimate the actual velocity is critical.
When gearing it critical to estimate the acceleration of the master because this is used to generate the feed forward signals for the slave.
We have an application where we use a motor with encoder to provide torque at low speeds (+- 5 Hz). The drive is Sinamics G120 in closed loop...
3,272
Hi all, i want to check incremental encoder ppr using oscilscope. how can i check ?
2,184
Dear Experts, Kindly Guide how to configure 1024ppr encoder in plc s7 200, CPU226, I want program in ladder logic don't know how encoder read ...
2,777
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
254