error 2023 when connecting excel to plc
NoLegalMoves
Jul 2012
Utah
I can't figure out what is not working...
Private Function OpenRSLinx()
On Error Resume Next
'Open the connection to RSLinx
OpenRSLinx = DDEInitiate("RSLINX", "PLC15")
'Check if the connection was made
If Err.Number <> 0 Then
MsgBox "Error Connecting to topic", vbAbortRetryIgnoreExclamation, "Error"
' OpenRSLinx = 0
End If
End Function
Sub Button1_Click()
Dim i As Integer
'write to PLC15
rslinx = OpenRSLinx() 'Open connection to RSlinx
'Loop through the cells and write values to the CLX array tags
For i = 0 To 9
'Get the value from the DDE link
realdata = DDERequest(rslinx, "CLN_823L31_3101_SPT[" & i & "],L1,C1")
'If there is an error, display a message box
If TypeName(realdata) = "Error" Then
If MsgBox("Error reading tag CLN_823L31_3101_SPT[" & i & "]. " & _
"Continue with read?", vbYesNo + vbExclamation, _
"Error") = vbNo Then Exit For
Else
'No error, place data in CLX
Cells(i, 2) = realdata
End If
Next i
'Terminate the DDE connection
DDETerminate rslinx
End Sub
' OpenRSLinx = 0
End If
End Function
Sub Button1_Click()
Dim i As Integer
'write to PLC15
For i = 0 To 9
Else
End If
Next i
DDETerminate rslinx
End Sub
Did you ever find a solution to your Error 2023? I am having the same issue.
sorry i dont think so.. i stopped working on this a while back
NoLegalMoves,
Looking at you code there are some discrepancies, please see below.
Here a list of items that I would check and/or modify:
1) Check that you have a valid DDE Topic in RSLinx named "PLC15"
2) In [Private Function OpenRSLinx()] - Replace "vbAbortRetryIgnoreExclamation" with "vbExclamation"
3) Comment out [Dim i As Integer] - Don't Need This
4) Uncomment [OpenRSLinx = 0]
5) Verify that "CLN_823L31_3101_SPT" is a REAL and the number of elements in your array matches, in your case the For i value or 10.
6) Cells(i, 2) = realdata is reading from the PLC to Excel not Writing to PLC. To write the "values" back into the PLC, you would use something like this:
DDEPoke rslinx, "CLN_823L31_3101_SPT[" & i & "]", Cells(i, 2)
7) If you have more than "1" worksheet, you MUST specify the worksheet that you want to read to or write from.
Hope this helps.
K
Hi there, I'm new to plc programming and was wondering why I get this error code when I run my simulation for these temperature sensors? What I'm...
23
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
16
323
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
98
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
184
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
143