Error 8097: Controller Error - CPU Slot Mismatch

dung.ho

Member
Join Date
Oct 2023
Location
Houston
Posts
5
Error 8097: Controller Error - CPU slot mismatch [0x05][0x46] [0xC00C0001]

I got that error above when I was trying to download my programming to Controller. Please let me know if anyone knows how to solve this error. Thanks.

Capture.PNG
 
Welcome to the PLCTalk forum community !

I don't recognize the software environment shown in that screenshot. What controller make and model are you using ?

The error message of course suggests that the CPU is configured for a different chassis slot than it is physically located in, so check the configuration against the physical location.
 
That looks like Machine Edition software for a GE or Emerson PLC.

Here's what the help file has to say about it.

CPU slot mismatch
(PACSystems RX3i only.) The HWC has the CPU in a different location from the one that it really is on the RX3i. A fatal configuration mismatch is logged in the controller Fault table.

"HWC" stands for HardWare Configuration, which is a map of the modules and the addresses assigned to them.
 

Similar Topics

Hello, I am having an issue downloading to a GE 90-30, CPU 364, I have configured the EGD following a documentation on GE Ethernet Global Data...
Replies
0
Views
912
One of our customers had a Rx7i redundant Controller system for their plant. Due to some power failure the Controllers power was interrupted. Now...
Replies
1
Views
4,437
I’m getting this error: I’ve pulled the battery and left it out for a few minutes. It’s been a while since I’ve ran into this and I can’t...
Replies
1
Views
969
I am trying to download a program that will only change the integrated IP address in a rx3i IC695CPE305. The logic is equal. The current IP is...
Replies
9
Views
5,454
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Replies
15
Views
234
Back
Top Bottom