Steve Bailey Lifetime Supporting Member + Moderator Join Date Apr 2002 Location The boondocks of Western Massachusetts USA Posts 8,593 Aug 24, 2010 #16 You need words for data and bits for boolean instructions. Both types can coexist in the same program.
lonegator Member OP L Join Date May 2008 Location Missouri Posts 15 Aug 24, 2010 #17 I understand that. For the DI and DO, I'm using bits. But for the AI and AO, I need to use words. I just don't understand why I'm receiving an error when pointing to a word with an integer data file.
sthompson Lifetime Supporting Member + Moderator Join Date Jan 2007 Location Vernon, BC Posts 1,852 Aug 24, 2010 #18 lonegator said: I need words though for the data I'm trying to transfer/display. Click to expand... The example you gave in your first post can only deal with Addresses specified to the Bit level. i.e. N30:0/1. This can only represent 0 or 1. You need to use Instructions that deal with Words. Like this; Stu....
lonegator Member OP L Join Date May 2008 Location Missouri Posts 15 Aug 24, 2010 #19 Ah...there's my answer. Thank you!
sthompson Lifetime Supporting Member + Moderator Join Date Jan 2007 Location Vernon, BC Posts 1,852 Aug 24, 2010 #20 Go to the Allen Bradley Literature page. http://literature.rockwellautomation.com/idc/groups/public/documents/webassets/browse_category.hcst Search for; The SLC500 Addressing Reference Manual - 5000-6.4.23 The Instruction Reference Manual - 1747-RM001G-EN-P The User Manual - 1747-UM011G-EN-P You need to do some quick studying on SLC500 Addressing and Instructions. Stu....