Error when go onlne with SLC 5/04 Processor
JNS
Apr 2009
UK
26
I am trying to make some modifications on the existing plant application. I have set up the demo system in the office to test these modificaitons. I only have Power supply, PLC and rack similar to the plant but I DO NOT have any IO cards which exist in plant application. As soon as I download and try to put PLC in run mode it goes in to FAULT mode and returns following major fault message.
"Module 2 which is required for the user program is detected as missing or removed."
It seems that program is looking for IO cards that I dont have installed in the rack on demo system at my office. Is there anyway I can go online and test modifications by disabling these IO cards or is there any other alternative to get rid of this fault and put processor in RUN mode?
Thanks,
JNS
To add to what Mickey and Bernie have said, your chassis size must match (there's no way to disable chassis size checking), and you don't want to disable slot 0 since you are using the modular SLC.
since we don't know ALL about your system, here's another approach that might help – particularly if the chassis size on your desk doesn't match the chassis size in the field ...
instead of using "real-world" input addresses such as:
I:3/5
consider using "dummy" binary addresses while you experiment ... for example:
B11:3/5 might be a suitable substitute for the address given above ...
do the same thing for "real-world" output addresses too – such as:
B10:4/11 might be a suitable substitute for O:4/11 ...
once you've "proved out" the logic, you can use the software's Search-and-Replace feature to switch back to the "real-world" outputs ...
yes, this approach takes more effort than just "disabling" the I/O modules – but it's the only realistic method we've found that will overcome having the "wrong size" chassis to work with ...
I'm trying to compare strings in Studio 5000 on an Allen Bradley 1769-L33ER and came across this weird incorrect string comparison. Neither of the...
50
Hi All, I bought an old machine and I'm trying to get it running. It's a Pemas injection molding press running a Sigmatek control system with a...
30
Hello, When I try to read from the PLC, the following error occurs: There is no project name. Failed to read the intelligent function module...
63
Hello everyone I have the next issue with FactoryTalk Linx, when i configure the Ethernet driver and try to find the IP Address of the PLC Device...
57
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
172