ET200L problem
eams2010
May 2009
Alex
26
Hi All,
I have an ET200L module with part no. 133-1BL01-0XB0. I'm trying to connect it to a CPU317-2 PN/DP through profibus. The Problem that I can not find this part no in the hardware, so I can not add it to the hardware configuration. I searched in the internet and found the GSD file for this module, I installed it but still can not find it in the hardware.
I'm using V5.5.
regards
You can find it in the HW Catalog:
"6ES7 133-1BL0*-0XB0
Digital I/O 16DI x 24 VDC; 16DO x 24 VDC, 0.5 A, non-expandable, send capability for direct communication"
I dont understand what goes wrong for you.
Have you tried to drag-and-drop the abovementioned module from the catalog to the Profibus network ?
What error message do you get when you try ?
Yes I draged and dropped the module to the profibus network. I adjusted the address to be the same as the hardware address. saved and compiled, then downloded the hardware configuration to the PLC. What I got is SF, BF, and the error in the diagonistic buffer is the found module is not matched with the insterted one.
This is Siemens lingo for many possible error types. It can be that the DP slave is not accessible at all.
Attached the Error I got
It is working now
I do not kn ow what was the problem
I did the same as I'm doing every time and it worked
Thank you
How do I do This???? We are into PLC training and intend to show CPU Redundancy on Siemens S7 412 2DP cpu's. I have following Hardware (a)...
8,810
Does anyone have a source for old Siemens ET200L Profibus Modules? I have several that are bad and need to be replaced. I don't want to replace...
5,633
Hi I have an ET200L with an SC expansion 2 analogue input cards on slots F and G. The weird thing is, that Physically, the current inputs...
2,112
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
48
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...