ET200SP BA module gives io access error.
Smeagol
Aug 2020
Mordor
I have an installation that looks like this https://i.imgur.com/uR7hxki.png , everything works perfectly except for the ET200SP module.
I looked at the diagnostic status and it told me the offline and online configuration was different, i checked this and it was. The PLC buffer gave "I/O access error" on all the inputs from my ET200SP.
I tried to chenge the module to what we actually have in the cabinet wich is the BA version instead of the configured ST and wwhen i wanted to use the "change device" function it gives me this error: https://i.imgur.com/1a4ws5S.png
When i go through with it and dowload to device the system error persists. These are the I/O modules i have on the ET200SP, these are also physically there: https://i.imgur.com/VT2TA8t.png
This setup was used in another installation of ours but there we had the ST module instead of the BA but im hoping that its something else. any ideas?
That is not an error in the second image. TIA just warns you that the BA module has less functionality than the ST module.
N.B.
Not sure if OS 1 is a good name for an IO Device. There are limitations to what you can call a PN IO Device. Dont think you can have spaces in a Device name.
Usually the Device name is automatically converted to follow the syntax, but I dont like that the name is not the same as one has chosen in TIA.
N.B.
I changed the name to something better without any spaces and it actually worked. Thanks for the tip
Hi all, Happy belated turkey day! I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a...
635
Good evening guys, Please, I need help. This is my first time working with RS485 comm and I dont know what to do. Please, see attached files. I...
418
Hi , I have never used an decentralized i/o before but now I have approximate 90 3wire sensors on a relative small space away from my s7-1200. I...
1,325
In the termination "server module" there are holders for three glass fuses. Is this just for convenience or are the fuses needed? If so, what are...
879
Sorry if this is a stupid question, I am not as familiar with Siemens hardware as I am Allen Bradley. Customer specified that we use an interface...
1,318