Hi all,


Happy belated turkey day!


I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a cable from the RTU unit terminals, from there a cable goes to each of the meters. Technically, we have a star network. We use no resistors currently.



We are experiencing drops to one of the devices. And I think we may need termination resistors here.



My question, where to put these? At the two meters, AND the PLC end?


Thanks guys!
 
Hi Jesper,


RS485, baudrate 19200. Distance not sure, but I imagine 10-20 meters for each device.



Do you recon we should put the two meters in series, or rewire our cabinet such that both cables terminate directly to the CP?


Thanks!
 
Thanks Jesper, I will check it out.


Can't use Profibus plugs unfortunately, all devices are just screw terminals.
 

Similar Topics

I have a system with an ET200SP controlling a Profinet network already pre-established. Am I correct in that I can add a Modbus TCP/IP node and...
Replies
2
Views
1,908
Hi all, I have being trying in vein for the past 4 weeks to get a modbus master block to work on my IPC427. I have exhausted google search in...
Replies
12
Views
4,098
Hello! Does anyone have working sample for Siemens modbus master on ET200SP remote io rack or knowedge how it can programmed on step7 classic...
Replies
2
Views
2,248
Sorry if this is a stupid question, I am not as familiar with Siemens hardware as I am Allen Bradley. Customer specified that we use an interface...
Replies
5
Views
1,314
I have an ET200sp module (16x DQ - 6ES7132-6BH01-0BA0) that has no diag light on it. Everything on either side is lit up just fine. I've run a...
Replies
2
Views
1,425
Back
Top Bottom