ET200sp -> Fanuc R30ib/r2000ib communication
adrianedelen
Mar 2021
USA
I have an et200SP with the 1512SP F-1 cpu that we need to talk to a Fanuc robot.
The bot has a R30ib controller and also has the Ethernet IP Adapter package.
getting the profinet package for the bot is not really an option, and using an AB plc is also not an option.
Is there any way to communicate IO between the robot and plc directly?
We have a Prosoft EIP-PND gateway, which so far I have gotten to work with TIA but cannot get to communicate with the robot.
thanks.
thanks.
Is the gateway an EIP scanner or adapter? I assume adapter to adapter communication isn't possible.
Siemens has some EIP blocks you can use. See this example for the EIP Scanner. As a warning, it only supports unicast messaging. Multicast must be able to be disabled on the robot side.
thanks.
IIRC, can't the robot's EIP package be set as either adapter or scanner? With that Prosoft gateway, you'll want to make/try the robot the scanner.
Hi all, Happy belated turkey day! I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a...
631
Good evening guys, Please, I need help. This is my first time working with RS485 comm and I dont know what to do. Please, see attached files. I...
413
Hi , I have never used an decentralized i/o before but now I have approximate 90 3wire sensors on a relative small space away from my s7-1200. I...
1,318
In the termination "server module" there are holders for three glass fuses. Is this just for convenience or are the fuses needed? If so, what are...
872
Sorry if this is a stupid question, I am not as familiar with Siemens hardware as I am Allen Bradley. Customer specified that we use an interface...
1,314