ET200SP OPC communication using Kepserverex
kazmi1215
Feb 2019
Tampere
Hello,
I am doing the OPC communication of ET200SP using Keserverex v4. If I use the PLCSIM with TIA portal v15.1 and S7-300 (as no option of ET200SP) as the device in Kepserver, it works well.
When I use the same configuration with actual hardware then Kepserver gives error that "Device is not responding". What should I do?
Thank you
Is that an ET200SP Profinet IM, or is it an ET200SP CPU (like 1512SP) ?
If Profinet IM, you need an OPC Server that can act as a Profinet IO Controller. I dont know if Kepserver can do that. Simatic Net can. You need a license for Simatic Net Profinet IO Controller.
If ET200SP CPU, then you can do as you can with an S7-300 CPU, except for this:
Slot is 1, not 2.
You can only access non-optimized DBs.
PUT/GET access must be released in the CPUs hardware configuration.
The v4 server is so old I am not sure that it can talk with the ET200 anyway. You might try downloading the V6 server ans see if you can get that to work in demo mode. i know that other users have connected to the ET200 successfully. with V5 and V6
Agree with both comments so far.
Since you mentioned a 300 and PLCSIM: if you're trying to connect to the PLCSIM of the 1500, I very much doubt that Kepware will work, in any version. I think you'll need a real CPU, or possibly PLCSIM advanced.
With Nettoplcsim it should work with standard Plcsim, with some limitations.
Plcsim for S7-300/400 works always, not-optimized mode in S7-1200/1500 works also always (Put/Get must be enabled).
Optimized access maybe problematic. With Siemens software like the Simatic.Net OPC-Server works with Nettoplcsim, all 3rd party drivers for 1500 which I've tested fail with Nettoplcsim/Plcsim in optimized mode. I guess Plcsim uses a different object model or different access keys. But sometimes Siemens software itself fails to connect to Plcsim (without Nettoplcsim), WinCC 7.3 with TIA V14 Plcsim does not work.
Hi all, Happy belated turkey day! I have an ET200SP PLC with serial unit. We read out date from two energy meters using modbus RTU. We run a...
633
Good evening guys, Please, I need help. This is my first time working with RS485 comm and I dont know what to do. Please, see attached files. I...
414
Hi , I have never used an decentralized i/o before but now I have approximate 90 3wire sensors on a relative small space away from my s7-1200. I...
1,320
In the termination "server module" there are holders for three glass fuses. Is this just for convenience or are the fuses needed? If so, what are...
872
Sorry if this is a stupid question, I am not as familiar with Siemens hardware as I am Allen Bradley. Customer specified that we use an interface...
1,316