Ethernet comms with SLC 5/04?
pablo2000
Aug 2004
29
Hi Guys,
Can anyone suggest a way of getting a SLC 5/04 to talk over ethernet? I am installing an Ethernet network for about 10 AB SLCs and Logix 5000 PLCs. I need to add an existing skid onto the network. It has an SLC 5/04 and PV 1000 (2711-T10C8). I thought I could just swap the processor for a 5/05, but the PV can't communicate on serial to Ch 0 of the 5/05. Is there a way of either getting comms between my specific model of PV or of getting the 5/04 onto the ethernet.
Someone has suggested the 1761-NET-EN. Would this work?
Any help much appreciated.
Pablo2000
Hi ,
i see only one method for this ,
Add your SLC5/04 to Ethernet by using a 1761-NET-ENI (this is very simple to do),you'll have to use a software " NET CONFIG UTILITY" to coorectly set up your 1761-NET-ENI.To get this software you can take a look at AB.COM web site . so you just have to connect your SLC DF1 port to 1761-Net-ENI DF1 port.
If you change your processor to 5/05 ,it will not be possible to communicate through DF1 port ,because PV serial port is only an auxiliary port used generally for printers(this PV is for DH+ networks).
good luck
If on your logix 5000 plcs you mean the control logix system, if any of the racks have 1756-enbt cards (ethernet) i presume they will, you could also fit an 1756-dhrio (datahigh way) this would comm over the dh+ comms on your 5/04. the control logix rack is then used as a gateway.
cheers
myles
Since you now have the 5000, you can also add a DHRIO module in the 5000 rack. This allows you to leave the existing 504s on the DH+ and then you can go online with the 504's over the network.
I have a SLC 5/05 with really slow Ethernet comms. It is on a network with three Proface screens but comms is just as slow when I connect directly...
3,931
Hi friends, I have a Slc 5/05 1747-L551 processor that is communicating (was communicating) with a panelview 700 plus 2711P-B7C4D1 thru DF1. Bubba...
6,408
I have two SLC 500 5/05E processors on a subnet with a Delta motion controller. I am using OPC and Topserver for I/O comms and Wonderware for HMI...
6,657
I have slc 5/05 on a network with a static address(DHCP and BOOTP disabled). Recently had lightning strike which took out router and new router...
2,751
Can anyone suggest why the Ethernet port on my SLC 5/05 is sometimes very very slow when communicating with RSLogix? I have the SLC on a network...
14,077