How many Ethernet/IP nodes can you have on a 1756-L71 processor? The AB catalog shows "N/A" for the number of nodes and 500 for connections. The L81, for example, shows 60 nodes and N/A for connections.

I have a customer with a lot of VFDs and remote I/O on an L71, and I am wondering how much more I can add.

Thanks.
 
The number of nodes supported on the network will depend on the Ethernet module you add to it; an ENBT, or EN2T, or EN3T. You can also add multiple Ethernet modules, or ControlNet modules.

The number of Connections are the number of I/O devices the controller can support.

You also have to consider the performance you will get out of a module; the faster you ask for data, the harder the module has to work. You might get a 1756-EN2T to run all 128 possible Ethernet nodes if they're at 20 ms RPI, but not at 5 ms.

I've done a 1756-L71 system with 110 I/O connections through a single 1756-EN2T at 10 ms and it ran well.


The 1756-L8x controller has the Ethernet port built into the CPU, so that's probably why they list the number of "nodes" directly.
 
There are some capacity estimation tools, and this sort of thing is a great question to get your local RA sales office involved in.

Good luck !
 

Similar Topics

Hello, A while ago I modernised a magazine gathering / filmwrapping machine. This was a fairly big project for which I used an Omron CJ2M as the...
Replies
7
Views
2,612
We are in the process of upgrading our ancient Westinghouse motor buckets to the Eaton Freedom series unit. The new Eaton buckets are offered with...
Replies
4
Views
3,851
I plan on using a CompactLogix 1769-L16ER-BB1B , to control 3) PowerFlex 40 with a 22-COMM-E communication card in them. I took notice that in the...
Replies
22
Views
17,978
Hi all, I'm designing a project using a CompactLogix L33ER PLC, connected via Ethernet to several PowerFlex 525 VFDs and a Red Lion HMI. As far as...
Replies
4
Views
3,921
I am using RSNetworx. I do not have the EDS file for one of my EtherNet/IP nodes. Can I still add the node without an EDS file? If so, how do I...
Replies
2
Views
3,125
Back
Top Bottom