I have few Profinet slaves connected to S7-1200 over Profinet.
I wish get alarms and disagnostics from the devices. (IO-Link Masters).
Can someone share simple example code?
Thanks!!
Thanks MK42 but.. the "LIOLink_Diagnose" FB works only for Siemens IO-Link masters and not for third party IO-Link masters.
Does anyone has an example to get diagnostics/events/alarms from third party IO-Link masters?
Thanks for your help!!
You can get diagnostics using the RDREC block, which is all the Siemens FB will be using. There's very little information as to what that information means however, unless the literature from the third party manufacturer will have it.