I've been in this business that I rarely get excited about something new but I just finished a project in 1 hour.
The project was as follows. An existing SLC-5/05 was controlling 13 VSDs with Analog outputs. The customer redid all of the panels and somewhere along the long more than 25% of analog outputs got fried. No analog output module was available in time so I used a WAGO 750-880 using CoDeSys 2.3.9.44 (brand new) with WAGO's Modbus network configurator to connect the 13 drives (all had Modbus TCP) to one of the WAGO ports. I had the SLC-5/05 read and write EIP to the WAGO. The actual drive commissioning took about 10 minutes(!). It was the data mapping to/from the SLC and setting up the VSD's that took the other 50.
Kudos to WAGO on this one...
OK. I'll leave you alone now...
The project was as follows. An existing SLC-5/05 was controlling 13 VSDs with Analog outputs. The customer redid all of the panels and somewhere along the long more than 25% of analog outputs got fried. No analog output module was available in time so I used a WAGO 750-880 using CoDeSys 2.3.9.44 (brand new) with WAGO's Modbus network configurator to connect the 13 drives (all had Modbus TCP) to one of the WAGO ports. I had the SLC-5/05 read and write EIP to the WAGO. The actual drive commissioning took about 10 minutes(!). It was the data mapping to/from the SLC and setting up the VSD's that took the other 50.