Exhaust inside hazardous location panel
DaveW
Apr 2005
SoCal
389
I have a bank of solenoids located inside a purged enclosure in a Class 1 Division 1 hazardous area. The problem I have is that because the solenoids exhaust inside the panel, water can accumulates over time and may cause a problem. I've been told to run the exhaust to the exterior of the panel but not sure if this will cause a problem with the hazardous classification. I also want to install a dryer and air filter at the air supply end hoping to eliminate the water problem altogether but just to be safe, how would I fix the exhaust problem?
The idea of a Class 1 Div 1 enclosure is to allow for expansion but at the same time arrest the flame before it exits the enclosure. If you exhast to the exterior of the enclosre you will need to do it through some type of flame arrestor.
Since this is a purged enclosure, I assume there is a spring loaded exhaust port, can you pipe the solenoid exhaust to somewhere near this exhaust port? Then it should be carried out with the exhaust stream. If you pipe the exhaust to the classified area you may need a flame arrestor or detonation arrestor, I would check with your enclosure mfg. or perhaps your insurance carrier, before making any modifications.
Ken
Would anybody have an Autocad Electrical "Exhaust Fan Symbol" they would share? I can't find any that fits my needs, and I just don't want to...
2,845
In "Green Manufacturer Magazine" I seen a company in Washington State that uses exhaust from a dust collector to turn a low rpm generator to...
3,362
I am on a jobsite we inherited from previous integrator. One issue the customer has is the PID control of a 30hp exhaust fan moving 1000 cfm of...
4,402
I know this has nothing to do with PLCs. I just was wondering if anyone could steer me in the right direction. I got a soldering exhaust fan out...
4,387
I'd like you to meet my IO_Link Block, Fred. There are a couple of SSVs outside of Fred's AOI whose main purpose in life is to prevent me from...
156