BoxerBrats said:Another problem I saw yesterday, I have one section where there are 2 buttons (both are momentary) I use set / rst contacts to latch them in my probram. So basically button 1 latches, and button 2 unlatches... the problem is no matter which button I push it sends it to the same input.... I have checked both buttons have diffrent adddress, and everything looks right in my logic...
Do you use the PLC to set and rst the same contacts the screen uses?
ie. If TS ON = C100, TS OFF = C101, do you have a SET C100 or C101 and RST C100 or C101 in the PLC?