Good Morning ,

I'm trying to get a Ramp Pushbutton to work in a way that when the operator either presses the ramp button once or he keeps his finger on the ramp button that I get pulses that will go thru a ONS , consistently . I tried to set up a ramp to try it , but I'm having a hard time understanding it. I found tech notes , and the help for it , but I still don't truely understand it. I am correct in thinking that when the operator keeps their finger on it , it will continue pulsing on and off , correct ? What type of setting would I want to accomplish this ?

Thanks so much for your help ,
 
It isn't so much pulsing as it is adding to the destination tag. The tag itself doesn't pulse on and off. It simply says that as long as the button is depressed add "x" value to the tag at the specified interval.

The action of the button is an "output" (an action) where it sounds like you are treating it as an input that toggles on and off.

OG
 
Honestly, I try to do everything I can in the PLC vs with the HMI software. The PLC just has a lot more flexibility. Wouldn't be hard to set up a rung that starts a TON when they push the button (and use the TON DN bit in an XIO so it resets itself and keeps running if they continue to hold it down), have the PRE at 500-1000ms, and have it add whatever value to the destination tag every time the timer DN bit turns on.

You could fairly easy even set up logic to have the value added/subtracted increase the longer they hold the button down if they have a large range they have to move around in.
 

Similar Topics

As the title says, all of the client HMIs at the plant freeze up for about 5-10 minutes everytime I or a vendor make new routines or new tags in...
Replies
0
Views
1
Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
Replies
5
Views
104
Hello, I have a panelview plus that reads from 4 different PLC's. 2 of these used to be Micrologix PLC's and someone else went and updated them to...
Replies
3
Views
133
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
92
Hello all, I'm having trouble opening an application. After clicking open I'm prompted to login and after putting in username & password it...
Replies
0
Views
93
Back
Top Bottom