factorytalk view me shuttin down

enyew

Member
Join Date
Mar 2016
Location
soest
Posts
2
Hallo,

I have problem in running runntime application in factorytalk view. After loading the application the application shuts down when the run application command is excuted. anybod out there who can help me on this? thanx
 
Hi and Welcome to the Forum!

Have you any Security set up on the Initial Display?

An instant shutdown would typically be seen where the Initial Display has a Security Code assigned to it. The application is always started with the Default user logged in. If the Default user does not have this Security Code assigned to them then the Initial Display cannot load.

You then either remove the Security Code from the Initial Display or assign the Security Code to the Default user.

General practice would be to leave the Initial Display with no Security Code to allow the application to load with the Default user. You can then restrict access from the Initial Display to other Displays as required.

Regards,
George
 

Similar Topics

Hello, I have a panelview plus that reads from 4 different PLC's. 2 of these used to be Micrologix PLC's and someone else went and updated them to...
Replies
3
Views
73
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
62
Hello all, I'm having trouble opening an application. After clicking open I'm prompted to login and after putting in username & password it...
Replies
0
Views
86
Has anyone found information on using the variable message file? I keep looking for documentation on how to implement the message file name as a...
Replies
0
Views
72
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
5
Views
256
Back
Top Bottom