Hi,
currently working on a big project with several integrators involved. Just wondering if there's a rule of thumb of how many topics/shortcuts can I have pointing to the same PLC. Every area has a different developer who is using their own shortcut but the destination PLC is the same.
Thanks
 
While judicious use of extra shortcuts can improve communications efficiency a tiny bit, unless you are looking at tens of thousands of tags, I would stay away.


Each new shortcut (at least in older versions of FTView) use at least one connection to the processor, and connections running low can become a huge issue. The L8x Processors handle things so much better than anything earlier it may not be a problem.


You might never see a problem with an L8x CPU, and an EN2T or better module, but other devices, like the CompactLogix line are very connection restricted.


On the development side, that seems to be a plain nightmare. Why use different shortcuts everywhere? Just pick one and stick with it.
 
We're using L84S with E4TR module so we should be OK on that front.

I was wondering from more practical point of view or recommended/right way to do it. Haven't worked with v11 yet and previously we always used only one device shortcut for the exact reasons you described. Also the other developer parties have created separate HMI servers (still residing on a single physical server as we have only one licence with unlimited displays) to split the project, which is again something we never used to do even in larger applications (previous versions of FTViewSE) so was wondering if those recommendations/guide lines have changed in the recent version

Thanks
 

Similar Topics

Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
45
Hello all, I'm having trouble opening an application. After clicking open I'm prompted to login and after putting in username & password it...
Replies
0
Views
82
Has anyone found information on using the variable message file? I keep looking for documentation on how to implement the message file name as a...
Replies
0
Views
69
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
5
Views
241
Hello, I'm using FactoryTalk View ME V10. I created a valve as a global object with multiple parameters and when the object is being used at the...
Replies
2
Views
159
Back
Top Bottom