Hey guys, I'm new to the automation world and hoping you guys can help me out. I have a HMI that has Factorytalk SE installed and activated. The customer wants an additional HMI just in case the current one breaks on their current machine. Can I somehow use the same serial number and product key from the old HMI to the new HMI?
 
Depending on your setup, you may can install factorytalk activation manager on a server on your network and put the SE Client activation on it. You will then need add this server to your Activation Path on both client machines (Just click "Update Activation Path" on the Find Available Activations page, click add server, and enter in the servers IP address). This will share the license and give it to the first client that tries to connect. Sounds more complicated to set up than it really is, and works great if you have a server that is always on (such as a server for historian) on your PLC network.
 
I assume this is a stand-alone SE HMI?

You can buy a USB dongle from AB to tie the activation too. Then you can transfer it back and forth pretty easily.
 

Similar Topics

Has anyone found information on using the variable message file? I keep looking for documentation on how to implement the message file name as a...
Replies
0
Views
34
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
5
Views
221
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
Replies
0
Views
56
Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
Replies
2
Views
110
We are a water/wastewater plant, collecting realtime and manually entered data. We have been using FactoryTalk Historian (OSI PI) for real time...
Replies
3
Views
148
Back
Top Bottom