Fanuc 90-30 - Genius Bus controller failed

Hal9000

Member
Join Date
Jun 2010
Location
London
Posts
140
Hi there,

I have Genius Bus controller failed after a power outage i.e. the COMM LED is off indicating it hasn't received a configuration from the PLC. The GBC was replaced for new module but the customer still has the same issue. i.e same LED status.

Does the new GBC module need to be re-configured ?
Can Proficy Machine Edition configure the GBC or do I need legacy software i.e. Logicmaster 90-30 software or a Hand-held Programmer ?

Will power cycling or re-loading the PLC application code recover/re-configure the GBC?

The PLC itself is indicating a healthy state i.e. for - Power, OK, Run, all of these are green

I'd be grateful of any thoughts to help a stressed customer on a Friday afternoon!

Many thanks,

JD
 
Configuration of the bus controller module is included in the PLC's hardware configuration. The module is compatible with Proficy Machine Edition. Was the battery good when the power failed or did you have to download the program to get the PLC to run? The PLC must be stopped when you download a hardware configuration. There is a check box to include hardware configuration in the download that doesn't appear when you start the download process while the PLC is running.
 
Hi Steve,

Many thanks for your reply.

I'll find out what the customer has done (if anything) I'm getting my information 3rd hand at the moment but they may ask if I go to site to assist.

They had a long power outage so its feasible the battery wasn't in good shape, although all the PLC LEDs are green.

many thanks

Justin
 

Similar Topics

Dear all, I'm facing a strange problem in genius bus communication.my system configuration is 90-30 hot redundant (software redundant) CPU372...
Replies
5
Views
3,357
Hello all, first time post, although this site has saved me many times cheers! OK... my problem. On site we have a GE 90-30 with 364CPU and a...
Replies
3
Views
2,355
Hi I have Genius communication between RX3i and GE Fanuc 90-30 system using IC94BEM331 Genius controller. I referred the manual but its not...
Replies
8
Views
4,328
Years ago, we had a PLC-5 here running some "Supervisory" Utilities Logic. It had (still has) a Wonderware front-end. It was reading multiple...
Replies
12
Views
3,627
Hi, Need some help with a 9070 PLC issue. It is a genius bus installation that performs periodic autotesting on field I/O. I am getting errors...
Replies
4
Views
1,235
Back
Top Bottom