We are running logix 5000. We had a plc fault on us. I cleared the fault as soon as i saw it and am now looking for the root cause of the fault. How do i look back at fault history? When i look in the major and minor fault is do not see anything showing there. Is there a way to find the fault after i have cleared them. Seemed to be some kind of communications fault. All of the drives in the program showed faults.
more info
i have went through the program and checked all of the fault code tags and they are not showing faults. it appears that the program is set up to clear these tags whenever you clear the fault. is ther anywhere else that you can see the fault history
As far as I know, you're out of luck. Always do a print screen before you clear the fault ;)
For the newer Logix processors you can insert an unprotected SD card when the processor is in fault and power cycle the processor and it will dump the MNRF (Major Non-Recoverable Fault) log to the card.
It may be a simpler option to programmatically trying to achieve similar results. It also allows you or another to quickly power cycle the fault and resume operations. You can then review the fault log later.
Regards,
George
Ot
It only takes a few seconds to read the fault. You could have taken a picture with your phone or print screen. I understand being busy, but busy doesn't mean take shortcuts.
That's easy to say after the fact, but there are certainly days/nights where it is much harder to do. I've been there and made the same mistake.
Bubba.
Is there a way to get the fault history from a SIRIUS 3RW4456 Soft Start through the HMI keypad? I've been through the manual but it is pretty...
744
Good afternoon all, I have the above HMI from AB with firmware v9, with the program created by an OEM. Their laptop is using view Studio v9 as...
2,265
Good Morning , I have a bank of Kinetix 6000 Drives that I'm getting faults on. I took notice in my ControlLogix , Controller Tags for the...
3,732
What happens if you let a minor fault keep logging on a 1756-L62S? Will it consume memory and crash the project? I received a call that a machine...
2,495
We sell a product that uses an Allen-Bradley Pico micro-PLC (bulletin 1760), which is actually made by Moeller. The device monitors a small...
2,331