FIFO with siemens S7-300 cpu's
Rverhoeven
Jun 2002
16
We have a priority energy system for 4 pump systems. only one pump system can be started at a specific time. The commands for starting the pumps however can be given at almost the same time. So the program has to "remember" which pump system was first. Therefor i thought i could use a FiFo, and there's the problem. i don't have a clue how a can create a FiFo in Siemens Step 7 (cpu type is S7-316)
Does anyone have an idea how to do this.....
An end is the beginning of something.......................
If have a look in your Program Elements, you will find a library, the path is:
Libraries \ Standard Library \TI - S7 Converting Blocks \ FC85
if you highlight the FC-block and press F1 you will get some help on how to programme it
Hope this helps you out :D
When you say:
do you mean the classic:
"Due to inrush concerns, no pump may be started within 10 seconds of another pump"?
If so, you don't need a FIFO, you need a Start Permissive.
Straight ladder (I don't know Step 7 specifically, but this code is pretty generic)
Step 1. Remember the Start Command (this rung will be repeated 4 times, once per pump)
START-1 START-1
CMMD PUMP-1 MEMORY
START-1 |
MEMORY |
Step 2. Create a one-shot of the pump starts.
Repeat 4 times.
PUMP-1
PUMP-1 oneshot ONESHOT
| oneshot
There are dozen different ways to do this - again, this is generic
Step 3. Run the Permissive timer when there are no pumps starting.
If a pump starts, reset the timer
PUMP-1 PUMP-2 PUMP-3 PUMP-4 +--- TIMER ---+ TIMER
ONESHOT ONESHOT ONESHOT ONESHOT | | DONE
-----|/|-------|/|-------|/|-------|/|-------|EN DN|---( )
| 10 |
PUMP-1 | SEC |
ONESHOT | |
-----| |-----+-------------------------------|RESET |
PUMP-2 | +-------------+
ONESHOT |
PUMP-3 |
ONESHOT |
PUMP-1 |
ONESHOT |
Step 4. The actual pump start logic (Repeat 4 times)
START-1 TIMER STOP-1
MEMORY DONE CMMD PUMP-1
PUMP-1 |
Does that help?
Now this code starts the pumps in scan order, not pushbutton order like a FIFO would. But presumably you won't be getting too many pump start commands during the "blackout period" for this to be an issue.
Thanx
Steffen and Allen. thanx for the information
To Allen:
I had to use the fifo cause there was a situation i didn't mention. sorry about that.
The system is also used in case of the EPS usage during powerout. in this case i have to remember which CPU ask for the power up command for the pump. it's a little more complex than i can write down here.
To Steffen:
i didn't know before but you can use the TI - S7 conversion functions in a normal S7 program.
hai can any one please let me know, how to use a FIFO & LIFO blocks with a small example ? I use SIEMENS S7-300:scratch:
6,164
Has anyone developed a FIFO program for the Siemens S5 PLC using Fastrak Softworks? Here is a very brief summary of the application: Gypsum board...
2,399
Is it possible to have a FIFO of strings in Siemens? I see that the FIFO instruction (FC85) manipulates words. Also, on a side note, are there...
2,542
I've had an old problem come back to haunt me; I'm using the S7 standard ATT/FIFO blocks for an accumulator, but for no apparent reason the FIFO...
7,246
Well HI all I am trying to use the FiFo/LiFo with a S7 300 and I am not to sure how to use it. I think I need the ATT table so that I could store...
4,537