Firmware change of CNBR E

shazad5444

Lifetime Supporting Member
Join Date
Feb 2014
Location
Houston
Posts
126
Friends,
I have existing CNBR Series. E, Firm ware Rev: 11.002 running in a redundant system, now I received new CNBRE with F/W 11.005. As our system is running on redundant system so their revision must be same, so I don't want to existing running system Primary PLC. Please advise how I can change firmware of CNBRE from 11.005 to 11.002.

Looking forward to hear.
 
Hello. I think you need to verify that the new hardware does support the old firmware. Then you need to go to the Rockwell website, download the desired version 11.002 of the firmware and then use the Rockwell Flash Programming Tools. The CNBR must be connected to a Logix Rack to which you can have access via USB or EtherNet/IP (and in very old system perhaps RS232C) so that you can communicate the Flash Programming Tool to the CNBR
 

Similar Topics

Good Evening , We have a number of Kinetix 6000 Servo drives ( fiber ) that fault out from time to time . I would like to change out the...
Replies
8
Views
5,313
I have written a PLC program using RSLogix5000 v. 19.11. But the customer has now requested that I convert it to v. 17.01, which is the version...
Replies
12
Views
8,762
Hello Everyone, I want to upgrade the firmware of Powerflex 40 from 5.001 to 6.002 can anyone tell me how can I do that?
Replies
0
Views
57
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
189
Hi all I have tried setting up the adc on a existing pf755 with studio 32 And want the firmware to update too the firmware on the plc is 12.01...
Replies
0
Views
42
Back
Top Bottom