"First Up" Hard Wired Circuit
Have the C1 relais controlled by your 4 relais.
so one contact of the four in series. (this will stop the turbine)
every contact goes to one relais simple parallel.
now you can see which contact will fail as one relais will stop activated. the one relais that stops has three contacts to keep the power on the other ones.
It means 4 DT contacts (industry standard)
I've gotta agree with Cheezy, when you lose Switch1 you lose all of your relays. Then it just becomes a relay race to see which one latches in first.
It's one thing to test it out on a sim, it's another to have to deal with the built-in latency of a mechanical relay.
Wouldn't it be any switch that drops out for that matter. I mean it seems it should have the same affect.
Hello,
Was wondering if anyone could improve on my "first up" circuit. I'm sure there is a way but cant quite get it!
What I've got is 4 switches pulling in a contactor. I wish to find which switch drops out first. I've done a program in statment list but was trying to do it hard wired as well.
The attachment shows what I have. First cicuit is the original. The rest is the wiring I need to capture the switch dropping out.
Is it possible to do it with just 4 relays rather than 8? I must be missing something!
cheers
Actually if you go strictly by your circuit, then all you have to do is see which of the 4 relays is no longer energized. That is the one that will be the culprit.
As an example, if relays 3 and 4 are off, then switch 3 is what went. If 2, 3, and 4 are off, then it was switch 2.
What I've done in the past is to use latching relays (like bce123 suggested) in place of R1, R2, R3, and R4. Arm the relays so they indicate latched. Then the first relay that is unlatched is the switch that caused the problem.
Now, if the circuit is not exactly like you shown and the entire circuit drops out if any of them open, then just looking at the energized relays won't work.
Hello! I have a control panel with two hard-wired push buttons. One button to switching on, and another one to switching off. And I have an HMI...
2,069
Hi, I design control systems where I use 24 VDC I/O. I always try to make my E-Stop circuit hard-wired (not relying on logic inside the PLC to...
9,806
Now I know from hearing through the grap vine that hooking up a hardwired Motor overload with a AC VFD is no good. I am not sure why you would do...
4,224
Hi - I'm a newbie to the PLC world but was recently asked if we could store more than the 2G that the CompactLogix 5370 allows by its max size SD...
1,342
It's Saturday, so I thought it would be amusing to look at times gone by, imagine if you had to carry this to site "IBM 5mb Hard Disk 1950's.
1,876