Flow metering problem
magicsmoke
Aug 2007
Minnesota
110
I know this isn't a PLC question, but I'm sure some has worked on this type of problem.
Problem I have a Hersey 1020 Totalizer with a Halliburton turbin flow meter connected to it when the pump kick on the Hersey Totalizer tells me that 46gpm is flowing and after one min. I should have 46gpm accumulated on my meter, but I don't I'm only getting 36.
If some one could help that would be great.
Magicsmoke
I glanced at google looking for documentation to help you dig in to it. I didn't see the actual Hersey site right away. Do you have the web address?
What type of signal connects the turbine to the Hersey?
Is this a digital electronic display or a mechanical display?
Stationmaster
Does it say 46 gpm for the entire first minute? Depending on the application, empty pipe, back pressure etc.... Flow rates can taper down to a sustained rate that is less than the start up rate.
I'm inclined to agree with Ken Moore. This issue is like comparing the readings on the speedometer on a vehicle (rate) and the odometer (totalised distance). If you view a speedometer which is reading 100 km/h you can't say with any justification "therefore I must have travelled 100 km in the last hour". It's not such a simple relationship - there are far too many other factors to be taken in to consideration.
Ken
usually for the meters u have something called k factor , this the number of pulses per unit volume , u should this number on the turbine meter and have it feed in the totalizer. u can get this number also from the calibration sheet if u have it.
Did u buy the totalizer intergrated with the turbine or seperate items?
This has been installed on our system for years and just started having problem's with it. I looked around and found the tag with the k factor and it was set right for that. Could the trubin be missed up and giving me false readings?
Turbines DO get messed up but if you're talking about a problem with the blades or prop, it should effect BOTH flow and total. The circuitry would be more suspect if you have a GENUINE discrepancy between flow and total.
Stationmaster
I couldn't find any docs online for the model numbers you gave. Can you describe the circuit? Signal type? etc?
Stationmaster
P.S. Hey wait a minute. You have books?
Had to dig deep but found the book found that some one entered the k factor backwards they went top to bottom which in the book they say bottom to top changed the k factor and everything is good. checked out 4 more and found they were wrong also.
Just a thought, signet flow meters have a k factor setting for both flow AND totalizer. They can be different. Maybe yours can too.
Marc
Good afternoon to all ( good morning and good evening if your on the other side) New project using two sets of rinsing overflow tanks (water...
1,815
We have a wash facility which uses a venturi to draw an iron phosphate chemical from a tank into a high pressure water line running at 160 bar...
1,756
Hello, I have this project that I need to connect a flow meter (http://www.powogaz.com.pl/pliki/prod...l_K_52_420.pdf ) to control a metering pump...
10,148
Dear all, i have been traped in a trouble, i need to creat a totalizer for flow metering in the plc, the signal is comming from flow transmitter...
3,891
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
191