Flow sensor issue with micrologix 1400 series B
Daniel Farfan
Oct 2019
Tijuana
Hello.
I am having an issue trying to read data from the flow sensor model FL-608 (Digiten) in my micrologix 1400.
I read that i have to use a HSC.
I used it, i think i configured it properly but i am run Mode but dont seen to work.
Can someone please help me? :(
have you evaluated your input frequency against your flow sensor frequency ? if sensor is faster than input, it won't work.
Sometimes you can even use a standard input into the standard program if the pulsing rate isn't needed very precise.
I will let others comment on how to work around hsc with a ml1400 but i think you should provide more details about what you have done.
Hi.
First i tried with an open contact of the input 0 (where the signal wire of the sensor is) and a counter but nothing i cant seem to make it work.
Then i looked for info and configured the HSC but nothing i cant read.
I tested it with an arduino and it worked.
But i cant seem to make in with the plc
I am doing something wrong but honestly dont know
Post details about the sensor, how it is wired, and your HSC configuration and its related program.
Ideally, ZIP the *.RSS file and attach it to your forum post, instead of using screenshots.
The MicroLogix high-speed counters were meant to count pulses then quickly trigger an event (or local output), and they do not have a built-in "Rate" mode.
Is your application intended to determine a flow rate from that sensor, or to perform a volume measurement by counting a total number of pulses ?
Hi.
You can see attached files of the characteristic of the flow sensor and my hsc configuration
The sensor is fl 608 of digiten
Square pulse
3 wires: 5 to 24 v to red wire
0v to Black wire
Yellow to signal wire
I can read the input voltage on + and - and also between signal and +
The applications is to read volumen depending on the signals and close a solenoid valve.
Thanks for your replies and help
No files appeared attached to your post.
What is the voltage you measure at the Input ?
How fast is liquid flowing through the sensor, and how many pulses per second do you expect that to generate ?
Can you see the input status change state, either on the LCD screen or online with the MicroLogix ?
How much volume do you intend to measure (how many counts) ?
Are you trying to measure the flow rate, total, or both?
See the attached quick start guide for the HSC. I've used this successfully for the ML1400 a number of times.
Ok, i have corrected some things and did "some" readings.
I powered the flow sensor to 24vdc and changed the plc com to 24v but i only read 0 and - 1
I have the MOV with HSC:0.ACC to L9:0 (long)
I Just want to fill bottles, i want to let pass certain amount of volumen of water, 355ml, 500ml, 1 L, 1 Gal
Hey guys, I am building a small prototype for a Coolant Dispensing System and need to measure the flow rate of water & chemical in the pipe in...
3,658
Hi all, I have an application where I have to measure air flow through a HVAC duct, as we have to ultimately maintain a certain rate of air...
3,228
Good Morning , I am new using a Keyence FD-Q Flow Sensor and Ethernet/IP NU-EP1. I am using it with a CompactLogix 1769-L18. I think I have...
2,459
By default my transmitter (GF Signet 9900) is scaled 0 GPM (4mA) - 100 GPM (20mA). I'm trying to figure out how determine my max value to get the...
17
4,659
Hi, I'm obviously pretty new to programing and automation. i was looking to get some helpful hints and maybe some steps in terms I could...
2,244