forcing bits on and off Logix 5000
showshocka
Mar 2011
USA
510
Gentlemen. I'm having trouble forcing a bit on in my logix5000 program. I see its not as easy as it is in the 500 program. When online the drop down menu will not highlight force commands to let me force any bits on. The input bit i need to force is coming from a PE that's causing a low level compensator alarm causing the line to stop, even when i have the PE reading my hand all the time. My histogram is still showing the it's losing it's signal. How do i do a simple force in the routine in the logix5000 program? Thanks!
When you right click on a input or output address, there is a Force On, Force Off, or Remove Force option. Just like in RSLogix 500.
You can only force Inputs/Ouputs. Pretty sure you can force tags which are aliased to Inputs/Outputs.
SINT, INT, or DINT? What do these mean?
These are data-types. They refer to the size of the word. SINT=8 bits, INT=16 bits, and DINT=32 bits
Not sure about why forcing isn't enabled for you, we don't have many 5000 proc's here. I've only had to add a rung here or there, never had occasion to need a force.
Once you set the force (tell the program what force state you want), then you have to enable forces.
2 step process.
You can only force a real I/O such as a push button, a solenoid or a valve, etc.
Furthermore you can force an alias -
as long as it's an alias of a real Input or Output tag
So, I'll bet you a box of donuts (like Ken Roach is used to say 🍻 )you're trying to Force a tag which isn't an I/O tag, and this isn't possible.
Double check the tag named I_3.11 and you will see it isn't a real I/O.
- fuzzy logic
Somewhere in the program the real input for that PE should be mapped to the tag you are looking at. A cross reference of the tag should lead you back to that input.
It might be leading somehow in logic to a photoeye, probably there in the "Map_Inputs" routine, but "I_3" is not the base tag for an input module.
The tag for the photoeye will have a base tag with a name something like "Local:5.I.Data[10]". That will be forceable.
Dear Fellows; I am working on a very old machine which is designed in GE 90-30 PLC system. I have some difficulties like 1. How a force to...
350
Control logix5000. If have an XIC on a rung with an OTE I can force the OTE on but if I force the XIC it doesn't turn on the OTE. Why is that...
26
6,770
Hi, I haven't used Unity for a while and have just fired it up to develop a good sized program. At first glance it seems that I can only force...
9,340
Hi. This is the first time I do a project with Rockwell PLC from scratch. I started a bit just building some AOI for a couple things I need to...
574
Hello, when trying to force two outputs nothing happened. The text ON appeared by the adress. It was also possible to force off, which also...
17
4,808