FT View ME, Versus Red Lion Crimson

AutomationTechBrian

Lifetime Supporting Member
Join Date
Jul 2013
Location
St. Cloud, MN
Posts
669
Ok, whoever it was who told me I'd find FT View limiting... you are SOOO right!

I put a Panelview in this project because I wanted the software on my PC, and this would be a good job for an Allen Bradley HMI. But some of the simplest design features in the Crimson are no where to be found in FT View. ....or at least I can't find them.

For instance: I told the customer I'd add an experimental feature on the HMI that would only be visible if a bit was high. That way, he could just push a button to remove it from the operator screen. Now... As far as I can see, that feature is not available in FT View. I can check a box to make something visible in the software, but I can't tie it to a bit.

Have I overlooked this feature in FT View?
 
Visibility in FTView is handled by animation. Right click on the object > animation > visibility. If there's an expression in the visibility animation, it supersedes the check box setting.
 
....or at least I can't find them.

You learned one of the most important parts of AB stuff - becoming a detective!

I've used both Crimson and FTV a lot over the years - they both have all of the features needed for "basic" hmi work, but the steps needed for each software package to achieve the same result are very different.
 

Similar Topics

I'm on-site trying to figure out what my customer has. The program in the Panelview Plus 700 is gone, and their machine is down. They were given...
Replies
29
Views
4,897
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
46
Hello guys please I want experience with this I am currently working on a scada project using FTView SE and I have an Ethernet IP local area...
Replies
0
Views
35
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
5
Views
210
I am using Factory Talk view Machine Edition Runtime HMI. I want to configure on button in such way that when i press this button I want to...
Replies
3
Views
147
Back
Top Bottom