JMA123 Member J Join Date Dec 2021 Location Laguna Posts 2 Dec 21, 2021 #1 Hi. I migrated panelbuilder32 hmi to factorytalk view. However character array is not supported in ftview. Appreciate your help how to map the plc tag of that character array to FTView string. Newbie here, thank you!
Hi. I migrated panelbuilder32 hmi to factorytalk view. However character array is not supported in ftview. Appreciate your help how to map the plc tag of that character array to FTView string. Newbie here, thank you!
widelto Member Join Date Jul 2005 Location Barranquilla, Colombia Posts 3,392 Dec 21, 2021 #2 I have not touched panelbuilder for many years, do you mean string array ?
Phrog30 Member P Join Date Dec 2006 Location Montgomery, Alabama Posts 1,048 Dec 21, 2021 #3 Bit and character arrays aren't supported, just as it says. In your case use a string, either memory of the HMI or PLC string.
Bit and character arrays aren't supported, just as it says. In your case use a string, either memory of the HMI or PLC string.