FTView ME - Acknowledge Alarms

Tracon

Member
Join Date
Oct 2016
Location
Nebraska
Posts
4
Hey guys,

I would like to be able to press a button on an HMI and have it both acknowledge an ALMD/ALMA alarm in the PLC and also acknowledge it in the Alarm List in the HMI. With a FT Alarm and Events server for FTView SE this would be a piece of cake, but unfortunately I'm running this on a machine.

My thoughts were to somehow use some type of PB to connect to a tag in the PLC to acknowledge the alarm there and also connect it to a macro to push the standard Ack Alarm button that you can link to the alarm list.

Would anyone know how to do that? Or have a better idea of a way to do what I am trying to do?

Thanks
 
While I don't use the ALMD/ALMA functions myself, there is a way to have a PLC tag acknowledge the alarms.

Go to Alarm Setup --> Advanced. Under there, put your PLC tag in the "Remote Ack All" box. Then set your HMI pushbutton to also use this PLC tag.
 

Similar Topics

Is there a simple way (VBA or macro language) to acknowledge ONLY the most recent alarm? I upgraded recently all the way from RSVIEW 32 7.60 to...
Replies
4
Views
676
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
Replies
4
Views
171
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
216
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
90
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
Replies
0
Views
88
Back
Top Bottom