Good day all,
my customer has panelview packed up and i have a similar one in stock and i have managed to upload the ftview me application (ver 5.10) from the damaged unit.
The hmi i have is preloaded with ver 8 firmware.
Is there a way to downgrade the hmi to a version that will run the 5.10 application.
thank you
Hi all,
i have setup my new panelview plus 700, running version 8.0.
My me transfer utility transferred my ver5.10 application no problem.
New problem, when the application is about to start on the panelview,
a resolution warning pops up to say the application's resolution is different to
the terminal resolution do you want to continue, i say yes it loads but the application is so much smaller than the panelview screen.
I checked in the application project settings and the resolution is set to the correct 640x480.
any ideas why this is happening and how to correct it?
thank you
Was the project built for a PanelView Plus Compact ? Does the message say anything about the resolution, or just that it does not match ?
There was a resolution checking feature (and warning) added to PV+ v8 firmware, but in general it really does detect that the application was built for a different resolution.
What are the exact part numbers / models of the old and new terminals ?
Yes it was built for panelview plus.
It says resolution of the application
Is different ro resolutionof the terminal
Old hmi was 2711p-t7c4d1 ver 5.10
New hmi is 2711p-t7c4d8 ver 8.0
I did some further testing and i tried a different application, also a ver 5.10 and this one loads and runs perfectly.
Not sure why the other one is small, because in the project settings it is selected to be the correct resolution for the panelview plus 700.
So it seems the problem is specific to this application only.
Hello guys please I want experience with this I am currently working on a scada project using FTView SE and I have an Ethernet IP local area...
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
173
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
224
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
95
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
92