FTView ME unsupported communications protocol
KingPresident
Aug 2015
Michigan
138
First time I've encountered this; a fellow controls guy here compiled the project into a .mer and downloaded the project. The panelview plus 7 challenged with a communications driver error. It prompted me with a 'Load anyway?' yes/no screen. I pressed 'no', and it kicked me out to the terminal menu. I reset the terminal and it again had the comms driver error. This time I pressed 'yes' just to see what would happen, and the project loaded and works just fine. I'm ok with the fact that it works, but not ok that I didn't solve the actual problem. Does anyone have an Idea? I confirmed setting in RSLinx Enterprise, and the Communications tab.
Would upgrading the firmware be the thing to do? Thanks.
It's probably telling you that there's a CPU in the comms schema that's not supported by the firmware on the terminal.
It works when you bypass the warning because the newer CPU doesn't have any comms-specific features that are incompatible.
To get rid of the error, I agree that upgrading the PV+ terminal firmware is the right approach.
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
171
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
220
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
90
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
90
Hello, I have converted RSView 32 to FTView SE 14 (I have tested FTView 12 before as well and there were some difficulties so I moved on to...
256