FTview MeStation :Can use Goto display button as momentary push button ?

minaykha

Member
Join Date
Apr 2009
Location
singapore
Posts
96
Hi Everybody,

is there anyway to use Goto Display button as a Momentary push button ?

When Goto display button is pressed, i need to change the HMI screen and at the same time i want to write a value to PLC program.

I am using Factory Talk Me station and Rslogix 5000 software.

Any Suggestion ?
 
Hi,

We use the 'Global connections' option and use the PLC if we need extra functions regarding screen control (see attached image).
You can then use the action of a button to control a tag in the PLC and then use that tag to write to your screen control. Note - you need to reset the screen WRITE tag value to 0 if you want to use the regular FT navigation...


Regards,

Rob

2014-01-10_093851.png
 
Hi,

I just normally check for it not equal to zero, then (after a delay) move zero back! (see screen shot attached)

Hope this helps!

Rob

FTV Scn Rset.jpg
 

Similar Topics

I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
Replies
4
Views
171
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
220
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
90
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
Replies
0
Views
90
Hello, I have converted RSView 32 to FTView SE 14 (I have tested FTView 12 before as well and there were some difficulties so I moved on to...
Replies
4
Views
256
Back
Top Bottom