FTView SE Development file empty

tlawson726

Member
Join Date
Nov 2023
Location
North Carolina
Posts
2
Hello all,

I have a .SED file from a customer that they want rebuilt into a ME. When I open FTView Studio (v13 CPR 9 SR 13), I go to View Site Edition (Local Station) and import the .SED into a new project. However, all of the associated folders that are created are empty. No global objects, no graphics, no images, etc. It's as if none of the elements from the HMI are included with the Development file which makes no sense to me. Is there something else I need to get from the customer to be able to open their HMI in Studio? Or is there some step I am missing within the myriad of FactoryTalk programs (App manager, Server backup and restore, something else)?

Screenshot 2024-01-18 100634.png Screenshot 2024-01-18 100647.png
 
SE projects aren't all contained within the .sed. You need the whole directory containing the .sed. Run the SE Application manager to make a backup. You want an .apb file.
 

Similar Topics

Hello guys please I want experience with this I am currently working on a scada project using FTView SE and I have an Ethernet IP local area...
Replies
0
Views
34
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
Replies
4
Views
179
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
232
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
96
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
Replies
0
Views
93
Back
Top Bottom