Ge-Fanuc 90-30 Cpu ram memory reset
aslan
Dec 2002
İstanbul
57
Hi. We have one machine which has 90-30 plc. Because of the some unusual alarm messages, machine manufacturer recommend cpu ram memory reset. How can i reset the cpu ram memory. PLC has eeprom for the control logic.
Aslan, you need to reset all the plc faults with Logicmaster 90 or proficy ME. Connect your computer to the plc with the cable and go online with the plc and go to the fault table and clear all the faults.
Clearing the faults does not "Clear the RAM".
You can connect to the processor and stop the CPU then in Proficy ME use the Target > Online Commands menu to clear all memory.
But as you say this system uses an EEPROM and if the OEM has set the system to "Copy Logic & Config" from there on power up, cycling power on the CPU rack will do the same thing.
But then it just may be that it looks to them that some retentive memory may have some incorrect data in it that needs to be cleared.
mzepeda, to clear fault table didn't solve the problem.
RussB, i will try your recommendation tomorrow. Thanks.
Dear Everyone I work with PLC GE-Fanuc. But I don't know that "PLC GE-Fanuc (Series 90-30 and VersaMax) can Online Edit Programming while...
3,054
I'm working on a 90-30 PLC which keep losing its program everytime it is powered down. We first figured it must be a battery issue, so we tried...
1,310
I am setting up a bench practice unit consisting of a 5 slot rack (IC693CHS397C), POWER SUPPLY IC693PWR330C, cpu 351,and one input and one output...
3,873
We recently purchased a IC693CPU352 module and it appears the internal time clock is static. I can set the time and date but once set it does not...
174
Hi guys. Im a total PLC noob. i suspect a dead 331 cpu. Unable to communicate with it using the LM90 start utility. But i could on another CPU...
2,933