I'm at a customer and they have bought a machine "as is" and it has a ge 90-30 siries plc with a 10 slot rack. In slot 10 there is a Horner 8 chanel thermocouple card. The problem is that none of the temps register in the plc memory. I can go online and change the value of a temp input and it will stay there.I can remove and/or short out the thermocouple and there is no change. It seem as if the back plane is bad but I'm not sure and could use some help determaning this. I have also replaced the input card with a new one with no change. The rest of the machine works well.
 
It sounds to me like the CPU has lost the hardware configuration.

Did you have to download the ladder logic to the PLC? If so you probably needed to also download the hardware configuration file. The hardware configuration file tells the CPU what to do with the data it gets from the module in each slot. The fact that you can write a value to the address where the temperature data should be suggests that the PLC doesn't know what to do with the data from the Horner module.
 
Hi, If the card type is IC693TCM302 then this card cumunicate
with the CPU with AQ AI and if some registers value was changed then the card will not run and will lost the configuration.
 

Similar Topics

Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
34
I have a CNC cutting equipment, all the components are Fanuc from the CNC CPU A02B-0307-B822, a PLC AIF01A and a panel i, on the panel i (operator...
Replies
1
Views
119
I want to buy this program if anyone has it. Absolutely no one has it officially for sale. My cpu is IC610CPU104B My mail...
Replies
2
Views
114
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
Replies
0
Views
107
We recently purchased a IC693CPU352 module and it appears the internal time clock is static. I can set the time and date but once set it does not...
Replies
5
Views
176
Back
Top Bottom