GE-fanuc PCM711

sandy5020

Member
Join Date
May 2012
Location
vadodara
Posts
112
90-70 system with pcm711 is communicating with daniel flowcomputer s600 but data is updating very slowly,,,any body got idea on this?
 
Maybe.
What do you call very slowly?
How much faster do you want to be?
How much data?
What protocol?
 
hello russ

in plc logic one sec timer is used to retrieve flow meter data but some times one sec delay is occuring and in scada is also another delay ,,,,but in flow meter data is continously updating,,,,how to improve this???/

am usiing rs485 modbus protocol, and 34 length registers are reading,

pcm is configured as basic
 
With the PCM711 and Modbus you should be able to get 34 registers very fast, maybe 4-5 times per second at 19.2 k baud.
Did you write the Modbus in the PCM or is this purchased from a third party?
Did this work better in the past or are you developing this now?
How does the SCADA fit in this, what/who is the SCADA. Does it communicate Modbus to the same devices? Who is the Modbus Master and who are the slaves?
 

Similar Topics

i have Daniel flow computer Flow boss (device ID-32) is communicating on RS485 with GE FANUC 90-70 PLC(PCM 711 card). The flow computer is getting...
Replies
2
Views
1,904
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
47
I have a CNC cutting equipment, all the components are Fanuc from the CNC CPU A02B-0307-B822, a PLC AIF01A and a panel i, on the panel i (operator...
Replies
1
Views
133
I want to buy this program if anyone has it. Absolutely no one has it officially for sale. My cpu is IC610CPU104B My mail...
Replies
2
Views
123
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
Replies
0
Views
118
Back
Top Bottom